Neutral Size for SFD
wrobotronic
Colorado
Would someone be so kind as to point me to where the NEC 2014 will indicate that the Neutral can be smaller than the ungrounded conductors for a 200A service to a SFD...
Basically, If I run 4/0 AL for my service what size can I make the neutral?
Thank you very much everyone....
Don't overlook 250.24(C) in regard to "minimum size"
Just so I am clear on this: My conductors are 4/0 Al for a 200A SFD service. Then by Table 250.102C1 My neutral (grounded conductor) only has to be #2Al?
My gut tells me im wrong on this. I have never sized a service per se, I have always just done what the drawings/ foreman have said. Normally, I use 4/0Al for 3 conductors and a #2Al for my grounding electrode conductor.
I am making this harder than it needs to be... which honestly needs to be my signature because I seem to post that statement quit a bit... :)
Thank you all for your help....
Think of the neutral as a white wire with an imaginary green stripe. It carries unbalanced current (white) or serves as a ground fault return (green). You can calculate the unbalanced current or do what everyone else does, just use 2/0. Why 2/0? Thats the way it comes with 4/0 4/0 2/0. Many code cycles ago the neutral was two trade sizes smaller than the ungrounded, so that practice still carries over, I need to look to see when this was changed, or maybe someone else will know
if you use 2 AL the inspector will not of seen that before, will want to see the calcs, and may look closer at your install.
I like to have my students understand the code and what the reasoning is.
You are correct in that a #2 AL is the smallest size you could run based on Art 250, however, 220.61 calculations may require a larger wire. You can perform the calculations (Mike Holt;'s home page has a nice calculation form in "Free Stuff") or, as Tom mentioned above, you could
use a 2/0AL and most inspectors would not question the reduction as it would be almost impossible for a 200 amp service to require larger.