If a neutral is required for equipment that is rated 480v 100 amp does the nuetral conductor have to be the same size as the feeder conductors or can it be 1 size less?
I used to be able to do it in under a minute, back in the days that the cube first became popular. Of course, first I had to “send in for” a copy of the solution. Probably cost me a whole quarter, not counting the 10 cent stamp. :grin: :grin:1793 said:So, Charlie b, what is your best time to solve the "Cube"?
If the neutral is being used in a situation in which it can carry as much current as the phase conductors, then in order to protect it from overcurrent it must be sized using the same process as was used to size the phase conductors. If the neutral is being used in a situation in which it can only carry the unbalanced current from the phase conductors, then it is not in danger of being damaged from an overcurrent condition.winnie said:The neutral conductor must be properly protected by OCPD, and the only OCPD will be those for the ungrounded conductors.
charlie b said:If the neutral is being used in a situation in which it can only carry the unbalanced current from the phase conductors, then it is not in danger of being damaged from an overcurrent condition.
chicar said:If you install the same size grounded conductor as your ungrounded conductors you will be able to sleep better at night.
BossMan20 said:there are few instances where you'd be able to reduce the neutral.