An existing install has a 1200 feeder (breaker set at 1040A and restricted access) with 3 parallel 500's per phase, a 3/0 EGC and 2/0 neutral. The EGC is sized per 250.122(F), and I had assumed the neutral was undersized because it could not be smaller than the EGC per 215.2(A)(2). However I am now seeing that the 250.122(F) requirements do not apply to the grounded conductor sizing requirements.
Assuming the feeder neutral loads are less than the ampacity of paralleled 2/0's, am I correct in thinking that the 2/0 neutral is ok despite the larger EGC?