Would someone mind checking me, I don't normally resize the grounded conductor, but I was asked to save some pennies.
I have EV chargers using 480V 3Ph requiring 4-wire plus ground. The largest one is 180kW with an input current of 240A and 300A MOCP. I'm using 350mcm for the phase conductors, and if I use table 250.122 per 215.2(A)(2), I could use a #4 for the grounded (neutral) and EGC. Does that sound correct?