I've spent the last 2 hours chasing my tail through the code book trying to answer this, and for some reason I can't find an answer. I figured I ought to ask before I pull out the little bit of hair I have left.
We're putting in a pair of new residential HVAC condensing units and in the process relocating them to the other end of the house. I'm planning to use a small 3R panel at the new location for combination OCPD and disconnect with a conduit home run to the main panel about 40 feet away. The units both run on 240V single phase.
I also want to power the required utility outlet from this panel (with its own breaker). Since this outlet is the only 120V load present, it seems like a total waste to run a #6 or #8 neutral (and I'm spending MY money on this one, so waste is a no-no!). Since that outlet is the only 120V load present, would it violate any codes if I ran a #12 neutral ? I could also take that neutral direct to the outlet and bypass the neutral bar in the panel if necessary.
Thanks!
D.
We're putting in a pair of new residential HVAC condensing units and in the process relocating them to the other end of the house. I'm planning to use a small 3R panel at the new location for combination OCPD and disconnect with a conduit home run to the main panel about 40 feet away. The units both run on 240V single phase.
I also want to power the required utility outlet from this panel (with its own breaker). Since this outlet is the only 120V load present, it seems like a total waste to run a #6 or #8 neutral (and I'm spending MY money on this one, so waste is a no-no!). Since that outlet is the only 120V load present, would it violate any codes if I ran a #12 neutral ? I could also take that neutral direct to the outlet and bypass the neutral bar in the panel if necessary.
Thanks!
D.