rszimm
Member
- Location
- Tucson, AZ
Something I've always wondered a bit about:
So I'm feeding a 240V 100A subpanel with #3 THHN. Two hots and a neutral (plus a ground). Every circuit on that panel is a 120V circuit. So there's no current from one hot to the other. All current goes through one of the hots and into the neutral. Isn't the neutral now seeing double the current? Is this a phase thing that I'm missing (i.e. if there's 100A on phase 1, 100A on phase 2, is neutral current actually 0 or is it 200A)?
So I'm feeding a 240V 100A subpanel with #3 THHN. Two hots and a neutral (plus a ground). Every circuit on that panel is a 120V circuit. So there's no current from one hot to the other. All current goes through one of the hots and into the neutral. Isn't the neutral now seeing double the current? Is this a phase thing that I'm missing (i.e. if there's 100A on phase 1, 100A on phase 2, is neutral current actually 0 or is it 200A)?