This is my first time, be gentle.
Is a neutral required to be ran to all sub-panels?
I?m looking at a 240 volt single phase service that has a sub-panel fed from it. The sub-panel?s only loads are two 240 volt circuits. Given that an equipment grounding conductor is required, must a grounded conductor also be ran to it?
200.2 is telling me ?all premises wiring systems shall have a grounded conductor?? I?m not able to find in any of the exceptions or prohibitions listed, a way not to require the contractor to install one.
What are your thoughts.
Is a neutral required to be ran to all sub-panels?
I?m looking at a 240 volt single phase service that has a sub-panel fed from it. The sub-panel?s only loads are two 240 volt circuits. Given that an equipment grounding conductor is required, must a grounded conductor also be ran to it?
200.2 is telling me ?all premises wiring systems shall have a grounded conductor?? I?m not able to find in any of the exceptions or prohibitions listed, a way not to require the contractor to install one.
What are your thoughts.