Going through some electrical stuff on grounding. Would this be a violation to connect the neutral buss to the casing at both of these locations?
See attached.
See attached.
My favorite utility-approved meter socket is made by Milbank Manufacturing. The PoCo covers seven states. Because of PoCo rules, a 200 Amp lever bypass socket is required for all single phase 240/120 Volt services, 200 Amp or smaller. The PoCo also requires a fifth terminal at nine o'clock for a plug on meter movement to access the neutral, even though I, as yet, am still waiting to see that actually used. Been waiting about 20 years.Are there meter sockets with a neutral that is not btlted directly to the enclosure (case)? If so, I have never seen one.
Are there meter sockets with a neutral that is not bolted directly to the enclosure (case)? If so, I have never seen one.
Any how. The Milbank commodity meter base bonds the neutral to the case with a labeled removable strap. Similarly, the fifth terminal is bonded to the case with a removable strap. So, without the neutral-case strap, the neutral can float. The lugs and bus are not directly bolted to the case.
Marky, FYI:
A spec sheet from Milbank is available by clicking here.
And I note, in this picture, the fifth terminal is lug connected. The latest one I installed I had to remove the guts as part of the existing service alteration, and I recall that the terminal was on a long strap down to the case.
Sure there are. We have to install metering for our PV systems in a couple of jurisdictions, and the neutral cannot be grounded in the cans.Are there meter sockets with a neutral that is not bolted directly to the enclosure (case)? If so, I have never seen one.
Also for "meter centers" there isn't a bond at each unit, but may be bonding jumper that is able to be installed/removed according to needs in the "mains" section.
Specifically, 2014 NEC 250.142(A) is telling you that the "non-current-carrying metal parts of equipment, raceways and other enclosures" are not restricted to being bonded to the Equipment Grounding Conductor only.Does section 250.142 Use of Grounded Circuit Conductor for Grounding Equipment, allow the of use of multiple neutral to case connections anywhere on the supply side of service equipment? And is there a limitation to the number of connections?
In this thread, you are looking at the LINE side of the Service Disconnecting Means where neither the Equipment Grounding Conductor nor the LOAD side neutral exist. There is only the "Grounded Service Conductor" . . . which the CMP are using the term "Grounded Circuit Conductor" to name, as they (the CMP) are also naming a few other situations ( 2014 NEC 250.142(A)(2) & (3) ).
For the purposes of bonding non-current-carrying equipment, the LINE side of the Service Disconnect grounded service conductor can be connected to as needed, and as many times as needed (like a LOAD side EGC).
Thanks for that explanation!