Trying get a better understanding of NEV.
I understand the voltage drop on the neutral causes a potential difference between the neutral and the earth where the utility is bonded to earth.
What I don't understand is why that voltage is supposed to be present even though the neutral at the service (and utility pole) is re-referenced to earth.
If the neutral is re-reference to earth (zero volts) then it seems like the only potential should be the voltage drop on the neutral since it was last referenced to the earth.
Any thoughts to make it more clear?
I understand the voltage drop on the neutral causes a potential difference between the neutral and the earth where the utility is bonded to earth.
What I don't understand is why that voltage is supposed to be present even though the neutral at the service (and utility pole) is re-referenced to earth.
If the neutral is re-reference to earth (zero volts) then it seems like the only potential should be the voltage drop on the neutral since it was last referenced to the earth.
Any thoughts to make it more clear?