belkymd74
Member
- Location
- Raleigh NC
- Occupation
- Director of Project Development Engineering
I've got an AHJ telling me that if I have multiple generators tied to an essential system paralleling switchboard that feeds multiple 4P ATS(s) as a separately derived system, that I need to bond at each generator location per NEC 250.30 versus bonding once at the essential switchboard paralleling bus. My thought has always been that multiple bonds can create objectionable circulating current and GF detection issues and is not desirable. It looks like the NEC allows the bonding to be at the essential switchboard paralleling bus starting in the 2020 code but this AHJ is enforcing the 2017 version whereby that doesn't seem to be allowed. Interested to hear your thoughts?