I almost hate to ask this question; I believe I should know the answers but, humbly admit that I need an education.
The scenario:
A 200A 120/208V 3 PH panel was noticed to have an arc between neutral and ground. The electricians measured 25A @180Hz of current, 1.047V between ground and neutral. The panels are served from an 600A riser duct which is fed from a 2000A service entrance switchboard <100' away and a double neutral. We have not checked the neutral connection, preferring to wait for a scheduled shutdown next week. I am not sure how the individual phase currents are loaded.
Question:
1. Is the arching N-G a sign of just the distance between the bonded neutral and the point measured i.e. Is the low voltage current flowing to ground because it is the shorter path?
2. Is the 180 Hz current is a combined frequency of all three phases?
3. Since there is a measurable voltage differential between N/G, would there likely be any negative impacts?
4. Besides checking the neutral for positive connection at the duct riser terminal and the service entrance neutral/ground bond, is their something else that should be checked?
5. Is this normal to begin with?
Thanks in advance for any input and....be gentle .
The scenario:
A 200A 120/208V 3 PH panel was noticed to have an arc between neutral and ground. The electricians measured 25A @180Hz of current, 1.047V between ground and neutral. The panels are served from an 600A riser duct which is fed from a 2000A service entrance switchboard <100' away and a double neutral. We have not checked the neutral connection, preferring to wait for a scheduled shutdown next week. I am not sure how the individual phase currents are loaded.
Question:
1. Is the arching N-G a sign of just the distance between the bonded neutral and the point measured i.e. Is the low voltage current flowing to ground because it is the shorter path?
2. Is the 180 Hz current is a combined frequency of all three phases?
3. Since there is a measurable voltage differential between N/G, would there likely be any negative impacts?
4. Besides checking the neutral for positive connection at the duct riser terminal and the service entrance neutral/ground bond, is their something else that should be checked?
5. Is this normal to begin with?
Thanks in advance for any input and....be gentle .