I'm trying to understand the principles behind a neutral to ground fault:
An OCPD would trip in a Line to Line, Line to Neutral, Line to Ground fault, and an overload where the current flow would trip the device.
But let's say a neutral becomes dislodged from an outlet pigtail and is resting against a metal box which is properly grounded.
Once someone plugs something in, the current would flow from line and return on the neutral which is now faulted to ground which would be the return path for the circuit. This wouldn't trip the OCPD because it's not an overcurrent situation.
However wouldn't this energize the entire EGC? Including all the metal studs in a commercial building without tripping the OCPD? Now in a GFCI circuit this would be stopped, but in a standard non GFCI 20A circuit isn't this an issue?
Am I understanding the theory correctly? If so what is the protection or standard to guard against this (aside from GFCIs)?
If I'm missing something please enlighten me.