NEUTRAL TO GROUND VOLTAGE IN DELTA UNGROUNDED

Status
Not open for further replies.

bobby ocampo

Senior Member
Why is it that the voltage to ground of center tap neutral in one leg of an UNGROUNDED SYSTEM of 240 volts line to line is 70 volts?
Why is it that the voltage to ground of a center tap in one leg if connected to earth is 0 volts or at least approaching zero of a DELTA CONNECTED TRANSFORMER?
What is the connection to ground of the neutral doing?
 

Attachments

  • NEUTRAL VOLTAGE TO GROUND EXHIBIT 1.jpg
    NEUTRAL VOLTAGE TO GROUND EXHIBIT 1.jpg
    58.6 KB · Views: 11
  • NEUTRAL VOLTAGE TO GROUND EXHIBIT 2.jpg
    NEUTRAL VOLTAGE TO GROUND EXHIBIT 2.jpg
    65 KB · Views: 11
I don't think a centertap of an ungrounded system will be predictably 70 volts to ground. Also this is not an allowed configuration under the NEC; the center tap is required to be grounded.

A center tap that is grounded is zero volts to ground under no load ... because it is grounded. It's more or less by definition.
 