I have posted this before, but I had a job with 120 VAC between neutral and ground. This was a 3 phase 4 wire, 45 KVA motor generator. The XO/Neutral was never grounded, at some point there was a short from a 20 amp ?A? phase circuit breaker to ground.
Readings were
At the MG distribution panel.
?A? - Neutral 120 VAC, ?B? - Neutral 120 VAC, ?C? - Neutral 120 VAC,
?A? - Ground 0 VAC, ?B? - Ground 208 VAC, ?C? - Ground 208 VAC, Neutral - Ground 120 VAC.
This was a skiff (SP) full of top secret, very sensitive electronic equipment with iron clad construction specs (that no one verified compliance to), this site had been there at least 10 years and no reported equipment failures. The issue was discovered when new equipment was being installed.
The biggest issue with high neutral to ground voltage in a PROPERLY installed distribution system is high voltage drop on the branch circuits.