Oh, yes. That's a violation. The neutral bar clearly has information stating what gauge of wire each size hole is for. You can't split a 1/0 to go into two holes, since the holes are not rated for 1/0 in this example. You'd need to use somthing along the lines of a QO100AN neutral lug adaptor.lmchenry said:this is done in the panel on the neutral bar.
lmchenry said:can a (one) neutral conductor be put under two screws? I know you cant put two under one screw per 408.41.
cschmid said:I believe what you are referring to is when they run in an SE cable to the panel and the aluminum neutral is seperated into to pieces and terminated under two screws..is that a correct statement..
It is important for inspectors and electricians to know that the lug pictured is rated at 70 amps. For more than 70, the lug no longer has "fingers" and will bolt directly on top of the neutral or ground bar.Dennis Alwon said:Yes and that is why you need a neutral adapter to terminate under the screws.
![]()
Dennis Alwon said:Yes and that is why you need a neutral adapter to terminate under the screws.
![]()
alaskan JW said:Do you have to use one of these on a egc that is to large to fit under one screw?