Plano12345
Member
- Location
- United States
Not sure if I'm in the right forum.
State of Texas
Highway illumination
single phase using 240/480 service
in Texas, lighting is typically on 480 V. We have two wiring options for roadway lighting.
1. 2 hots and a ground
2. 2 hots, a neutral, and a ground
The neutral allows dropping down to 240 for certain lights along your run, like for an underpass.
question: based on the NEC 2011, is the neutral a CCC based on what I described. Please go into detail regardless of the answer. This neutral concept confuses me at times, and I'm not sure when its a CCC when it comes to derating. I read the section in the NEC but I'm simply a novice in some areas.
Example: i have a conduit with 11 conductors on 4 circuits. 2 of the 4 are from description 1 (2 hots x 2). The other 2 are from description 2 (neutral and 2 hots x 2). One of the 2 circuits with the neutral only powers lights using 240. The other has lights being powered at both 480 and 240, varying by location. The final conductor is the one for grounding. Question is how many are CCC? Either the answer is 10 or 8, and I know that alters whether I use 70% or 50% for derating.
thanks in advance and I will provide more info or clarity as needed.
State of Texas
Highway illumination
single phase using 240/480 service
in Texas, lighting is typically on 480 V. We have two wiring options for roadway lighting.
1. 2 hots and a ground
2. 2 hots, a neutral, and a ground
The neutral allows dropping down to 240 for certain lights along your run, like for an underpass.
question: based on the NEC 2011, is the neutral a CCC based on what I described. Please go into detail regardless of the answer. This neutral concept confuses me at times, and I'm not sure when its a CCC when it comes to derating. I read the section in the NEC but I'm simply a novice in some areas.
Example: i have a conduit with 11 conductors on 4 circuits. 2 of the 4 are from description 1 (2 hots x 2). The other 2 are from description 2 (neutral and 2 hots x 2). One of the 2 circuits with the neutral only powers lights using 240. The other has lights being powered at both 480 and 240, varying by location. The final conductor is the one for grounding. Question is how many are CCC? Either the answer is 10 or 8, and I know that alters whether I use 70% or 50% for derating.
thanks in advance and I will provide more info or clarity as needed.