Re: NEUTRAL WIRE
I feel the need to enter this fray. I'll start by coming to the defense of ?Electrical Designers.? Several of my previous companies used that phrase to denote persons who (1) Started their careers as drafters, (2) Learned the techniques and rules of electrical design through training and on-the-job experience, and therefore (3) Receive assignments of increasing responsibility, including making design choices. I have always considered such people to be valuable members of a design team. But like all of us, they still have much to learn. Therefore, I suggest we show them the same kindness and patience that we would ourselves desire to receive.
Originally posted by petersonra: . . . . did you notice in his post the phase conductors are #2 and the neutral #12? Is this code?
No it?s not. I am sure that is why Mr. Christian wants to replace the #12 with #2. In fact, although the neutral current is limited to the unbalanced current in the phase conductors, there may be time periods during which the only things turned on are on one or two phases, in which case the neutral carries a full load current. I can?t imagine why anyone thought a #12 would suffice here.
Originally posted by roger: I must ask, who seals the design, wouldn't they actually be the person to pose this question too?
Not all design processed require an engineer?s seal. I once worked for an electrical contracting company that had its designers send drawings directly to its installers. For those cases in which the client or the local authority required sealed drawings, the work would be supervised by a PE.
Originally posted by petersonra: But I don't believe I can give him a succinct reason why, other than it does not meet code.
I believe I can, two succinct reasons, in fact. All conductors of the same circuit must be in the same conduit (or in the case of parallel conduits, each conduit must contain a full set of phase, grounded, and equipment grounds) because:
Reason #1:</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The magnetic field generated by any single wire in the set will be essentially cancelled by the magnetic fields generated by the other wires in the set. This is what Roger had alluded to, and Bob did not disagree. To install one phase in its own conduit, or to install a neutral in its own conduit, would generate a significant local magnetic field. This could influence electronic equipment in the vicinity, and could cause heating of the conduit itself (if it is made of a magnetically-permeable material).</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
Reason #2: </font>
- <font size="2" face="Verdana, Helvetica, sans-serif">An electrician performing a future modification or upgrade could come across this single conduit with only one wire, and noticing that that wire is connected to the panel?s neutral bar, might conclude (incorrectly) that it is an unnecessary spare wire and that it may be safely disconnected. The only safe way to work on a circuit is to know where all the wires are, and to know how to turn them all off at the same time.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">