Neutral Wire

Status
Not open for further replies.

iaov

Senior Member
Location
Rhinelander WI
Only if opened or not bonded. In a properly installed system you might read a few milivolts to ground because of resistence in the wire. Any more than that and you have issues.
 
If you mean a "true neutral", it carries the imbalance between the energized conductors.

If you mean the white conductor of a two wire circuit, then yes it carries the same amount of current as the energized conductor.

If it is the grounded conductor of a 3-wire circuit that is installed from a 4-wire circuit, Wye system, then the grounded conductor will carry a substantial amount of current.

Take a look at 310.15(B)(4)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
the AC voltage on the "neutral" (grounded) conductor is zero with respect to earth ground :smile:
That is true only for the neutral at the point where the main bonding jumper is located or for a neutral that is not carrying any current. All neutrals that carry current will have a voltage to earth that is equal to the voltage drop on the neutral conductor between the point of measurement and the main bonding jumper.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Does the neutral wire ever have voltage on it.

In relation to what?

The neutral wire in relationship to the EGC would have voltage of 0 or very nearly 0 depending on the voltage drop of the conductors.

The neutral wire in relationship to an ungrounded conductor would have a voltage equal to the system voltage.

Chris
 

charlie

Senior Member
Location
Indianapolis
Does the neutral wire ever have voltage on it.
Yes. There will be a potential from the current carrying neutral to the normally non-current carrying grounding conductor. The voltage drop will make the difference as well as the difference in sizes of conductors. As stated before, the voltage will be low but it will be there. It all depends on how much return current there is on the neutral and the other parameters. :)
 

quogueelectric

Senior Member
Location
new york
Yes it can have a few volts with reference to ground.
Depending upon its distance from the source and the load on the entire system it would not be unusual to measure 1,2 or 3 volts on a large commercial building with respect to ground from the neutral.
It is simply voltage drop due to a combination of the load and the resistance/length of the wire. This will also sometimes create a small spark/arc when you touch it to ground.
This used to mystify me when I was a first year apprentice in 84 and hardly anyone could answer correctly what caused the spark/arc.
 

wbalsam1

Senior Member
Location
Upper Jay, NY
Yes it can have a few volts with reference to ground.
Depending upon its distance from the source and the load on the entire system it would not be unusual to measure 1,2 or 3 volts on a large commercial building with respect to ground from the neutral.
It is simply voltage drop due to a combination of the load and the resistance/length of the wire. This will also sometimes create a small spark/arc when you touch it to ground.
This used to mystify me when I was a first year apprentice in 84 and hardly anyone could answer correctly what caused the spark/arc.

If any body should be an expert on voltage, it should be a cow.:D:D They certainly have to put up with a lot from untrained farmers doing electrical work.:mad::)
 