It may be a little unusual to have a 3 phase panel in a residence, but not impossible. If your panel is in fact 3 phase it is OK to have 3 hot lines to one neutral. But the hot lines must be indentified so they don't get mixed up. You don't want to load down the neutral by having the phases connected such that the neutral will be overloaded. Why don't you check to see if you have a 3 phase panel? If you can see where the power comes in the house, look at the wires coming in from the pole (if it is overhead). If it is 3 phase you will see 3 insulated wires and one un insulated wire usually used as a support as well for the other wires. If you have only a single phase service you will only see 2 insulated wires coming in from the pole. If you have an underground service, you may have to open the panel up and look inside there to see how many wires you have coming in there. It is IMPORTANT to remember that anytime you see a red wire on a circuit breaker in a panel and you happen to be moving wires around on breakers in that panel, you must be aware NOT to have the red wire on the same phase as the associated black wire if they are sharing a neutral wire. Also, you can use a meter to measure the voltage, if you have a 3 phase panel, you would measure 3 legs to neutral at 120volts and between any 2 hot legs, you will read about 208 volts.