Re: neutrals and lighting contactors
It's critically important that conduits that carry a hot to your switch (contactor) carry it's switchleg(s) back in the same conduit.
When you do so, all of the following requirements are met.
(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (4).
300.20 Induced Currents in Metal Enclosures or Metal Raceways.
(A) Conductors Grouped Together. Where conductors carrying alternating current are installed in metal enclosures or metal raceways, they shall be arranged so as to avoid heating the surrounding metal by induction. To accomplish this, all phase conductors and, where used, the grounded conductor and all equipment grounding conductors shall be grouped together.
The hot and the switchleg are the only conductors in the circuit in a branched off conduit to a switch. Draw the circuit on a piece of paper and it's clear that the neutral is not a part of the circuit when it branches off to the switch.