I have recently been involved in the following scenario.
A single conduit 3/4" EMT contains 5 single phase 120V circuits fed off a 208/Y/120V panel (3 phase, 4 wire). This conduit contained 7 #12 AWG conductors and one #12 AWG ground conductor.
I had immediate concerns and so separate neutrals were indicated to bring the number of conductors in the raceway to the count of 10 plus a ground.
I still have the concern of de-rating and installing a ground for each circuit for a total of 5 #12 AWG ground wires.
The point of conflict has arisen over neutrals in this scenario and whether they are current carrying. I can explain this via vector analysis and Ohm's law as yes, but I am unable to prove (argue) this point from a Code perspective.
HELP
Thanks in advance