neutrals bonded to ground or not?
cpbcpb
I've got one meter. three breakers. one feeds mobile home with additional panel inside
second feeds panel at separate building with ground rod
third feeds another panel which then feeds through breakers to 2 separate buildings each with panel and breakers and also to a dryer inside mobile home (not connected to mobile home wiring above but in same mobile home)
Should only the ground and neutral be bonded at the first panel or should they be bonded at any of the others?
to be clear everything going somewhere leaves through a breaker
everything is direct bury or in PVC conduit
one mobile home, three buidings, one dryer circuit
Re: neutrals bonded to ground or not?
by the way all the buildings share cable TV and network( saw a post that made that seem relevant)
The grounded conductor(neutral conductor) is grounded to the GEC at the first point of disconnect, with a few exceptions. Read 250.32 to make sure you are complying with the proper requirements for the separate structures.
Pierre
As Pierre stated, read 250.32. I believe that the cable TV and network provide continuous metallic paths and prevent you from using 250.32(B)(2). 250.32(B)(1) must be followed, requiring an EGC with the feeders to the separate buildings. Ground and neutral should not be bonded at these separate buildings.
If I understand your description correctly the mobile home is wired in violation of
225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure served that is on the load side of the service disconnecting means shall be supplied by one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
Tom Horne