electron mover
Member
While doing loop checks on a new DCS system in a power plant MCC center with the buckets removed; I discovered all the neutrals were connected in parallel from neutral stab to neutral stab and laid down on the ground buss in each section with 14ga wire.
Each control transformer's neutral is grounded where it is mounted in the bucket. The transformers are from 100 to 500 VA and 480V pri. to 120V sec.. The primary's on these transformers could be out of phase and there are over 50 cubicles in this center. It is possible that some of these transformers may share neutrals to some field devices.
This is an older installation from the early 70's and is a GE MCC. I see some risk here should the neutral become lifted off the transformer or become loose and yet have a return path through all the parallel neutrals and through the bonding wire back to the source.
Are my concerns legitimate? Dose anyone see any code violations here?
Thanks,
Electron Mover
Each control transformer's neutral is grounded where it is mounted in the bucket. The transformers are from 100 to 500 VA and 480V pri. to 120V sec.. The primary's on these transformers could be out of phase and there are over 50 cubicles in this center. It is possible that some of these transformers may share neutrals to some field devices.
This is an older installation from the early 70's and is a GE MCC. I see some risk here should the neutral become lifted off the transformer or become loose and yet have a return path through all the parallel neutrals and through the bonding wire back to the source.
Are my concerns legitimate? Dose anyone see any code violations here?
Thanks,
Electron Mover