Jserra55

New User
Location
ILLINOIS
Occupation
Electrician
I plan to install a subpanel to feed several circuits.the circuits will be connected to a manual transfer switch fed by a portable generator.the circuits are now in the main house panel,so,can I simply extend the hots to breakers/generator wires in subpanel and leave neutrals in main panel or do I need to have the neutrals originate in the subpanel along with the hots.the neutral in house meter base stays continuous in power outage.
 

bwat

EE
Location
NC
Occupation
EE
Sounds like there may be other things going on here as well, but see 300.3(B) about keeping all circuit conductors together. Would it be in violation of that?
 