- Massachusetts
In this thread Panel Rewire - Opinions, Please I had questions as to why there where neutrals on the ground bar, it turns out in this particular case there was a factory jumper between the Neutral bar and the ground bar so I was mistaken.
But some of the responses I got seemed to say that even with out the factory jumper it would be OK to land Neutrals on the equipment ground bar at a main panel as they are electrically the same.
This would mean you would be using the steel enclosure as a Neutral Conductor.
I feel this would be a violation of 110.5
And 250.118 provides for the use of other materials for grounding conductors.
I do not believe there is anywhere in the code that provides for the use of a steel enclosure as a "conductor normally used to carry current".
IMO it would be wrong to do an installation that relied on the enclosure and the main bonding jumper whether it was a screw or a strap to carry current other than fault current.
I would like to hear any comments on this.
310.14 provides for the use of Aluminum Conductor Material.110.5 Conductors.
Conductors normally used to carry current shall be of copper unless otherwise provided in this Code. Where the conductor material is not specified, the material and the sizes given in this Code shall apply to copper conductors. Where other materials are used, the size shall be changed accordingly.