The above caught my attention today on a job site when I was considering conduit fill / derating.2002 NEC
310.15 (B)(4) Neutral Conductor.
(a) A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(2)(a).
The below I am used to and the above almost would include all neutrals after more than 3 current carrying conductors.
Am I reading this right?
(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.