Generally speaking, all dwelling 120V kitchen receptacles must be supplied by a small appliance branch circuit. If this is a new receptacle, the current-Code-compliant answer to your question is no.Can a new gas range recepticle in a kitchen be fed from an existing lighting 15a circuit?
Yes, welcome.
You may get more than one opinion which is probably why you posted the question
In reading 210.52, I think by literal interpretation as Smart$ noted, the answer would be "no".
That said, I doubt many inspectors would have a problem with it.
Since the outlet can be on the counter top circuit, I doubt the need to feed it from a lighting circuit arises often.
210.52(A)(1) Spacing. Receptacles shall be installed such that no
point measured horizontally along the floor line of any wall
space is more than 1.8 m (6 ft) from a receptacle outlet.
(2) Wall Space. As used in this section, a wall space shall
include the following:
(1) Any space 600 mm (2 ft) or more in width (including
space measured around corners) and unbroken along
the floor line by doorways and similar openings, fire-
places, and fixed cabinets
(2) The space occupied by fixed panels in exterior walls,
excluding sliding panels
(3) The space afforded by fixed room dividers, such as
freestanding bar-type counters or railings
(3) Floor Receptacles. Receptacle outlets in floors shall
not be counted as part of the required number of receptacle
outlets unless located within 450 mm (18 in.) of the wall.
(4) Countertop Receptacles. Receptacles installed for coun-
tertop surfaces as specified in 210.52(C) shall not be consid-
ered as the receptacles required by 210.52(A).
(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry,
breakfast room, dining room, or similar area of a dwelling
unit, the two or more 20-ampere small-appliance branch
circuits required by 210.11(C)(1) shall serve all wall and
floor receptacle outlets covered by 210.52(A), all counter-
top outlets covered by 210.52(C), and receptacle outlets for
refrigeration equipment.
IMO, the space behind a free-standing range is wall space. If it were built-in, I would agree with you.210.52(B)(1) references 210.52(A)&(C). I see nothing in 210.52(A) stating that the space behind the range is considered wall space or (C) stating that it's considered countertop space.
210.52(A)(1) Spacing. Receptacles shall be installed such that nopoint measured horizontally along the floor line of any wall
I have never installed a gas range receptacle from the SABC.Can a new gas range receptacle in a kitchen be fed from an existing lighting 15a circuit?
How is it NOT wall space???IMO that's a stretch.
If it were wall space then the area dedicated for an electric range would also require a 120 volt SABC fed receptacle.
the floor line by doorways and similar openings, fireplaces,
and fixed cabinets
I agree a free-standing electric range installed between cabinet sections presents a conundrum![]()
Isn't a dishwasher typically considered built-in (to the cabinetry)?So would the area behind the dishwasher.![]()
What if the range is completely freestanding with no cabinetry on either side, would you count the wall behind it as wall space?In post #11 you posted the NEC definition of wall space to imply that it applies to the area behind the range. I'm merely saying the definition you posted it would then also apply to the area behind the dishwasher. I'm of the opinion that it applies to neither.
I think that it's safe to say that no one has ever been required to install a SABC fed 120 volt receptacle next to the 40 or 50 amp electric range receptacle in the space dedicated for the range which leads me to conclude that the NEC does not consider that to be wall space.
What I am saying is the Code does not specifically exclude the area behind a range as wall space.
Okay :roll: , but...Look at 210.52(C)(1) exception
Exception No. 2: Receptacles installed to provide power
for supplemental equipment and lighting on gas-fired
ranges, ovens, or counter-mounted cooking units.
The NEC specifies wall space criteria in 210.52(A)(2). Are you saying it is incomplete??? :huh:Maybe we need an NEC definition of wall space.
And you disagree???I once had an inspector say that a square Sheetrock enclosure around a lally column in a basement remodel was wall space if each side was greater than 6" (+6" * 4 = +24"). :roll: