Will quote the relevant text section first:
"Multiple power sources of the same type that are connected in parallel to form one system that supplied premises wiring shall be considered as a single seperately derived system and shall be installed in accordance with 250.30."
Is it the intent of this text to say that multiple generators shall be a separately derived system? Meaning it would be a violation to have a system that doesn't switch the neutral, and has the main/system bond at the main service disconnect?
"Multiple power sources of the same type that are connected in parallel to form one system that supplied premises wiring shall be considered as a single seperately derived system and shall be installed in accordance with 250.30."
Is it the intent of this text to say that multiple generators shall be a separately derived system? Meaning it would be a violation to have a system that doesn't switch the neutral, and has the main/system bond at the main service disconnect?