Stevenfyeager
Senior Member
- Location
- United States, Indiana
- Occupation
- electrical contractor
I am estimating a 200 amp 3 phase new service, 208 v. The business is a wood pole barn with sheet metal siding. I don't think there is any steel at all except the siding. My inspector said I need two ground rods for grounding and bond to the building if possible. I guess the grounding with the two rods is the only thing I can do? I may have to ground to the water line.?... Also, sizing for grounding elec conductor; 250.66 A says #6 Cu, but for my 200 amp, (using 250 AL), Table 250.66 says I need # 2 Cu. Can you please help me? Thank you.