Hello. I am new to this forum. I am writing here because I can't get a clear answer from people I work with around here.
Looking at a new 3000 ampere service for a school building. The plans specify 8 sets of 4 #500 kcmil THHN copper conductors for the service.
The calculations on the plans give a total load of 3740A and a demand load of 2651A.
All sets of 4 plus grounds are run in 8 separate conduits.
The main transformer for the building is Delta to Wye.
Based on the 2008 NEC, since this is a wye system and the majority of the loads are non-linear, the 'neutral' wire is counted as a current-carrying conductor.
If I use the 90 degree column for #500 kcmil I get 430A x 8 = 3440A. De-rated to 80% gives 2752A.
Can I protect these service conductors with a 3000 ampere breaker? Over 800 amperes, can't round up. Based on the demand factor, it looks like
the conductor ampacity is okay but I'm not clear about the overcurrent protection.
Any help is appreciated.
Looking at a new 3000 ampere service for a school building. The plans specify 8 sets of 4 #500 kcmil THHN copper conductors for the service.
The calculations on the plans give a total load of 3740A and a demand load of 2651A.
All sets of 4 plus grounds are run in 8 separate conduits.
The main transformer for the building is Delta to Wye.
Based on the 2008 NEC, since this is a wye system and the majority of the loads are non-linear, the 'neutral' wire is counted as a current-carrying conductor.
If I use the 90 degree column for #500 kcmil I get 430A x 8 = 3440A. De-rated to 80% gives 2752A.
Can I protect these service conductors with a 3000 ampere breaker? Over 800 amperes, can't round up. Based on the demand factor, it looks like
the conductor ampacity is okay but I'm not clear about the overcurrent protection.
Any help is appreciated.