I am thinking about adding a new 225KVA 3 phase, 208/120volt wye-wye connected transformer to a facility that presently has a 300KVA, 208/120 volt three phase wye-wye connected transformer on it. The loads on the building are less than before and will stay that way. After I complete my calculations and determine the size of cable required from the utility pole drop down location to the transformer and complete my calculations for the service drop from the new 225KVA 3 phase transformer to the MDP, I expect not to have to worry about resizing the electrical feeders from the MDP to the various subpanels since they have already been sized and this is not related to the size of the transformer, but only the loads that existed in the building at the time they were sized.
I am almost positive about this statement. Each segment of a distribution system is sized just for it's relative loads, not for what is upstream on different segments of a distribution system.
I know that making this statement is bold, but I believe it to be true.