NEW 4000A 480/277V SERVICE - CABLE LANDING CONCERNS

Status
Not open for further replies.

Ragin Cajun

Senior Member
Location
Upstate S.C.
My latest design project will have one of these.

My client managed to get his hands on a used Square D I-Line panelboard lineup. From Square D delivery would be well over a year. He will get his in January of the coming year! The shop providing the equipment had been around over 50 years and knows what they are doing. The only negative is I would have ordered one with a cable entry section like I used on previous projects. This one is set up for cable entry behind the main breaker. The bus bars are barely 24” from the floor! Any way you look at it the electrician will need ape arms. My concern is that the likelihood of conductor and primarily insulation damage trying to bend and shape large cables to connect to the bus.

Reference the photo of similar gear.

Originally, I was going to use 10 – 600 MCM per phase with a 3/0 neural. But, coming out of 10 - 3-1/2” PVC conduits from below will be a nightmare. At best, with all the different phases crisscrossing each other, avoiding damage to the insulation will be unlikely. And maintaining equal phase conductor length? HA! The service transformer is a pad mount that is only 20 feet away.

One night when I couldn’t get to sleep, I think I came up with what I thing is a workable solution! How about using 12 - 500 MCM in 3-1/2” PVC conduits and coming up out of the floor directly under the phase bus bars, each conduit with only it’s respective phase conductors! Minimal bending of the conductors to lay onto the bus above. Little chance of damage and no crisscrossing. And maintaining equal phase lengths possible. Each conduit would have 4 – 500 MCM same phase conductors.

The system 3/0 neutrals would be in their own 3 – 3-1/2” PVC conduits and terminate to the neutral bus.

Of course, NO ferrous metal ever between the separated phase conductors!

Thoughts?
 

Attachments

  • 4000 A gear.jpg
    4000 A gear.jpg
    406.4 KB · Views: 27
Your plan sounds sound. With grouped phase conductors the make up is much easier as no crossing over phases. This system works great with open bottom gear
 
Last edited:
I would check with the POCO as to how many conductors they allow. I remember one only allowing 10
 
Given the distance to the bottom I see no problem with putting a full set of 500s in each raceway and terminating on that bus. The conductor length issue is something else.
 
Originally, I was going to use 10 – 600 MCM per phase with a 3/0 neural. But, coming out of 10 - 3-1/2” PVC conduits from below will be a nightmare. At best, with all the different phases crisscrossing each other, avoiding damage to the insulation will be unlikely. And maintaining equal phase conductor length? HA! The service transformer is a pad mount that is only 20 feet away.

I assume that your mention of the distance being only 20 feet is in recognition that this makes getting equal lengths within the enclosure even more important than it might be otherwise? For example, a difference of X inches in length will cause ~5 times more current mismatch on a 20ft run than on a 100ft run, because the impedance of the X inches will be a 5 times larger portion of the run's total impedance on a percentage basis with the 20ft run.
 
I assume that your mention of the distance being only 20 feet is in recognition that this makes getting equal lengths within the enclosure even more important than it might be otherwise? For example, a difference of X inches in length will cause ~5 times more current mismatch on a 20ft run than on a 100ft run, because the impedance of the X inches will be a 5 times larger portion of the run's total impedance on a percentage basis with the 20ft run.
Exactly!

RC
 
The service conductors will go directly from the utility transformer to the main breaker.

The main breaker will be the service disconnect. It will have a shunt trip with push-to-trip in a Knox box outside.

The main breaker will get a new trip unit with maintenance mode and ground fault.

RC
 
I used DLO/RHW for a 1500 hp DC motor because of the difficulty in getting the conductors terminated in the available space at both the motor and the DC drive. That might make things easier for this installation too.
 