fastline
Senior Member
- Location
- midwest usa
Building a new building and having a 400A service brought over. They will bring the primary over about 300ft shy of the building and I will go underground with secondary for the entrance. I am trying to decide on two 4/0 entrances or just one. It looks like I would probably need 500mcm for a single shot.
I realize I would have 2 panels and such with two entrances but I think those panels are pretty standard, thus cheaper?
I am building a 60x96x18 and will have some light commercial and residential use in the building. I really need more like 300/100 for the separation of power but still debating.
I used to work for an electric co and now in engineering. If memory services, the entrance cannot exceed 3% Vdrop?
Also, I was considering options for a smaller neutral. My load calcs are figuring on same size neutral so I assume for reduced neutral, you have to consider hot at one resistance, then neutral as another?
I am also thinking about conduits here. Never any fun working with small conduit. I think I need to go to 4" for 500mcm? 3" for 4/0.
I have read here about "triplexed" 4/0. I think the stuff I was looking at was THHW and twisted but no common jacket. Does that sound right for conduit apps?
I realize I would have 2 panels and such with two entrances but I think those panels are pretty standard, thus cheaper?
I am building a 60x96x18 and will have some light commercial and residential use in the building. I really need more like 300/100 for the separation of power but still debating.
I used to work for an electric co and now in engineering. If memory services, the entrance cannot exceed 3% Vdrop?
Also, I was considering options for a smaller neutral. My load calcs are figuring on same size neutral so I assume for reduced neutral, you have to consider hot at one resistance, then neutral as another?
I am also thinking about conduits here. Never any fun working with small conduit. I think I need to go to 4" for 500mcm? 3" for 4/0.
I have read here about "triplexed" 4/0. I think the stuff I was looking at was THHW and twisted but no common jacket. Does that sound right for conduit apps?