Marco Nunzio
Member
- Location
- Canada
- Occupation
- HVAC Tech
Hello everyone, I recently replaced a 5HP motor, 208v 3ph 60hz, A - 14.3amps (exact specs as the old one) which runs a large return fan. Replaced the motor and pulleys, good alignment and belt tension, ensured correct 3ph voltage and started up motor. A fuse blows (Ferraz Shawmut Fes30 - a 30 amp fuse - believe it is not time delay). I replaced the fuse and removed the load from the motor and started it up again. Motor inrush amps on 1 phase to 15 amps and then dropped to 6 amps running (w/correct rotation for my application). Confirming my motor is okay. Put the belts back on the pulleys, which adds the load back to the motor. Flipped the switch and motor inrush amps jumped to 90amps and immediately blew a fuse again.
On the old motor, the inrush would be around 60 amps but would not blow a fuse, and then drop and stablize at about 15 amps full load running (just slightly overamping).
I'm thinking time delay fuses would be the fix to the issue as the motor inrush is blowing the fuse. And I need an electrician to change the fuse holder in the panel as they do not have time delay fuses that would fit the existing screw in type fuses now.
I've ensured continuity and similar resistance values across windings, ensured no direct shorts to ground and ensured proper wiring for 208v 3ph.
But before I go through all this work, something doesn't make sense to me as to why the new motor is blowing a fuse and would need time delay fuses and the old one did not, any explanation?
I have images of my motor nameplate, the motor starter, motor overload, fuses, and setup which I can send through email to give you guys some more info, can't figure out how to drop them from my phone gallery to the thread.
Any help/explanation is greatly appreciated, this one has me going crazy.
On the old motor, the inrush would be around 60 amps but would not blow a fuse, and then drop and stablize at about 15 amps full load running (just slightly overamping).
I'm thinking time delay fuses would be the fix to the issue as the motor inrush is blowing the fuse. And I need an electrician to change the fuse holder in the panel as they do not have time delay fuses that would fit the existing screw in type fuses now.
I've ensured continuity and similar resistance values across windings, ensured no direct shorts to ground and ensured proper wiring for 208v 3ph.
But before I go through all this work, something doesn't make sense to me as to why the new motor is blowing a fuse and would need time delay fuses and the old one did not, any explanation?
I have images of my motor nameplate, the motor starter, motor overload, fuses, and setup which I can send through email to give you guys some more info, can't figure out how to drop them from my phone gallery to the thread.
Any help/explanation is greatly appreciated, this one has me going crazy.