Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
Typically yes, especially if it is old GE.Replacing 200A breaker with new 300A breaker. Could there be issue with it psychically fitting in the board/frame size?
Would it be able to be replaced? What may have to be done in order for it to fit?Typically yes, especially if it is old GE.
I would think you would need to talk with someone at GE. Besides physically fitting you also need to make sure they make a proper bus/finger kit for it, assuming the frame sizes are different.Would it be able to be replaced? What may have to be done in order for it to fit?
Physical space and bus bar connection assemblies.Would it be able to be replaced? What may have to be done in order for it to fit?
It's Siemens.Typically yes, especially if it is old GE.
It's Siemens not GE.I would think you would need to talk with someone at GE. Besides physically fitting you also need to make sure they make a proper bus/finger kit for it, assuming the frame sizes are different.
Ok, replace "GE" in posts #2 and 4 with "Siemens" . I am somewhat familiar with Siemens, what sort of equipment is this? Is it a panel board or a switchboard?It's Siemens not GE.
Do you know at the existing breaker is? Is it a QJ?
Definitely not a QJ.
You need to know the model number of the existing breaker or if there is existing space for a 400A frame. This is what RFI's are for. Get a readable picture of the entire existing switchboard, or a copy of the original switchboard drawings.So how could anyone even accuratley price the replacment of this?
Site survey before you bid.So how could anyone even accuratley price the replacment of this?
If this is a plan/spec job…the author of the plans is responsible to work through this.So how could anyone even accuratley price the replacment of this?
I agree with your statement to a point. As design professionals, we do not always have the ability or the accessibility to find this information out as some places have underwriters insurance that will not allow us (designers) to open up panelboards or switchboards. But, knowing that, we should have the owner set up a time when their electrical contractor, or an electrical contractor to be there so they can pull the covers and gather said information. But again, we do not this information going in a lot of the times.If this is a plan/spec job…the author of the plans is responsible to work through this.
It is NOT your job to resolve this nor is it ALL the other bidders.
What happens if for what ever reason a 400 amp cannot be added, are you on the hook for suppling a new section.
Send an RFI to the GC informing him the plans are incomplete.
You do need to develop contacts for each gear manufacturer so when these type of issues come up you have someone to reach out to for solid answers.