Installation of receptacles/switches, has anyone ever had a job turned down due to the above mounting screws not torqued . Is there a procedure stated somewhere on torquing requirements for receptacle screws and switches.
 
Re: new building switch/receptacle installation

The only torque ratings are for the wire terminals not the mounting screws.

The NEC section would be 110.3(B) which simply requires us to follow the directions.
 