gsallor

Member
Location
Roseville, MI US
I am Looking to Install Electrical to some new sites at a campground, I've done many repairs to existing wiring but never the design of a new install. With the help of my supplier this is what they came up with, and I want another opinion on if this is adequate, basically its 24 sites with 50/30/20 pedestals. What they came up with is 3 200 amp circuits with 8 sites on each circuit with a 400 amp main. any help or recommendations would be much appreciated.
 

wbdvt

Senior Member
Location
Rutland, VT, USA
Occupation
Electrical Engineer, PE
Being an RV'r and seeing some of the rigs that are now coming into the campsites, my gut tells me that is too small. If you look at the larger rigs, that have 50A services, they usually have 2 air conditioners, residential refrigerator, electric fireplace, 2 or 3 tvs, washer/dryer, etc. and if you get 8 of these on one 200A circuit, I think there would be problems. 80% of 50A x 8 is 360A. I may looking at it wrong but that is my opinion.
 

gsallor

Member
Location
Roseville, MI US
12 kVA per site, with a 55% demand factor. I come up with 220 amps for 8 sites. That's assuming 120/240v

yes that is correct 120/240V. How old is this demand factor chart? Is it enough for new RV's? But all this also assumes all 8 sites will have 50A RV's Some will only be 30A.
So Much to think about, anyone else have any input/advise on this?

Thanks to all so far for your input, given me lots to think about
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
yes that is correct 120/240V. How old is this demand factor chart? Is it enough for new RV's? But all this also assumes all 8 sites will have 50A RV's Some will only be 30A.
So Much to think about, anyone else have any input/advise on this?

Thanks to all so far for your input, given me lots to think about

The demand factor chart is from the 2017 NEC. The kVA per site was in increased in the 2017 from 9.6kVA per site to 12kVA per site for sites with 50 amp receptacles.

You would have to know exactly how many sites are getting 20,30, and 50 amp receptacles before you can do a load calc.
 

gsallor

Member
Location
Roseville, MI US
The demand factor chart is from the 2017 NEC. The kVA per site was in increased in the 2017 from 9.6kVA per site to 12kVA per site for sites with 50 amp receptacles.

You would have to know exactly how many sites are getting 20,30, and 50 amp receptacles before you can do a load calc.


Its 24 total sites with 50/30/20. What was recommended by the supplier was 400A main an 3 200A circuits with 8 each pedistals. When I calculated earlier per the NEC Chart I came out to 220A for the 8 sites each (55% demand) And I think it was like 410A for the main for all 24 sites with I think 43% demand. Is that adequate even being slightly over?
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
Its 24 total sites with 50/30/20. What was recommended by the supplier was 400A main an 3 200A circuits with 8 each pedistals. When I calculated earlier per the NEC Chart I came out to 220A for the 8 sites each (55% demand) And I think it was like 410A for the main for all 24 sites with I think 43% demand. Is that adequate even being slightly over?

I come up with 516 amps for the feeder/service for all 24 sites.
 

gsallor

Member
Location
Roseville, MI US
Ok I come up with two different numbers depending how you calculate it

Mike holts Formula

24 sites @50A = 230,400VA (50A = 9600VA X 24) Demand Factor 43%
230,400VA X .43 = 99,072VA / 1000= 99.072KVA (net computed demand load)
99.072KVA = 412.5A

Second Formula

24 sites @ 50amps =12KVA x 24 = 288KVA
288KVA x .43 = 123.84KVA
123.84KVA = 512.5A

Which is right?
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
Ok I come up with two different numbers depending how you calculate it

Mike holts Formula

24 sites @50A = 230,400VA (50A = 9600VA X 24) Demand Factor 43%
230,400VA X .43 = 99,072VA / 1000= 99.072KVA (net computed demand load)
99.072KVA = 412.5A

Second Formula

24 sites @ 50amps =12KVA x 24 = 288KVA
288KVA x .43 = 123.84KVA
123.84KVA = 512.5A

Which is right?

It depends on which NEC you have to follow. 9.6 kVA per site if you are under the 2014 and 12kVA if you are under the 2017.
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
My 2 cents, since I’ve put in a couple.

I wouldn’t sweat it if it was a regular campground as not every owner is at there site on any given day.

But if this is a campground used for special events (ie. Fairs, Racetracks, etc) these camping events will see almost 100% of the owners using their campers. So take some consideration. The demand factors are a little low. (About 15% from my experience with one of our campgrounds installed 15 years ago.

Campground expansion I'm working on now alows 6 of the same combination you’re talking about on a 200A Breaker. But as you’ve said many will still only be using the 30A (3600va) That should give us a long time before we see all campers using the 50A (12,000va) in our installs now. By then the equipment will probably need replaced anyway.
 

kwired

Electron manager
Location
NE Nebraska
My 2 cents, since I’ve put in a couple.

I wouldn’t sweat it if it was a regular campground as not every owner is at there site on any given day.

But if this is a campground used for special events (ie. Fairs, Racetracks, etc) these camping events will see almost 100% of the owners using their campers. So take some consideration. The demand factors are a little low. (About 15% from my experience with one of our campgrounds installed 15 years ago.

Campground expansion I'm working on now alows 6 of the same combination you’re talking about on a 200A Breaker. But as you’ve said many will still only be using the 30A (3600va) That should give us a long time before we see all campers using the 50A (12,000va) in our installs now. By then the equipment will probably need replaced anyway.
Where it is at does impact things to some extent.

Public campgrounds will see a large variety of units, a mix of 50 and 30 amp units plugged in. They likely are full on Memorial Day , July 4, and Labor day, and during any local celebrations, and down south maybe even a few other times between Oct - April.

Private campgrounds may have less variety in some cases. Fairs, racetracks, and similar places may actually see more higher end units that utilize a 50 amp supply than a general public campground does.
 