magictolight.com
Senior Member
- Location
- Indianola, Iowa
Went on a warranty call back today. Have a nutone central vac system which is blowing a dedicated 20 amp circuit, one leg in a 3 wire circuit. Name plate full load amps is 12.5. 120 volt system. Square D Homeline breaker panel, 200 amp service. System draw 63.5 amps at start up and levels out at 10.5 amps, voltage drops from 120.5 to 117.5 and then stabilizes at 119 volts, GFCI receptacle is 25' from breaker panel on #12 stranded THHN. This is a cord and plug connected appliance. Vac has been tripping circuit 2 or 3 times a week for months now. Only tripped once for me, was on site early in the a.m. and probably had not run yet today. Tripped only on the first start and the other 10 or 12 starts ran fine. Was hoping that I could increase the amp rating of the circuit to accomodate the inrush but can't find a good spot in the code that will let me do it with a 20 amp receptacle, Article 210. Thought I might get away with cutting the cord cap off and hard wiring also. I hate the idea of hacking this thing together but I am at a loss. Any ideas?