Circuits pulled from OSRP to RP3.
These new circuits intercept below RP3. RP3 is not gen backed panel and we need the fridges and freezers backed up. I have pulled the "existing" four circuits(in RP3) down into the trough below RP3 and are tied onto the new circuits from OSRP. There is a #10 grn pulled in with the four circuits.
My question is.....Do these circuits now tie in only with the #10 brought over .....or can the #10 tie into the ground bar in the panel? Thanks much!
 

Attachments

  • E-Circs.jpg
    E-Circs.jpg
    91 KB · Views: 5
Thanks Roger. I was getting hung up on "all conductors....same panel". In this case, I DID need to pull a ground(grn) along with them right?
Yes, unless you were planning on using the metallic raceways as the EGC.
 