I was wondering if you could put like a 2'' pvc conduit on top and bottom of a new panel in a house for the homeruns? Is there a code to doing that? And would it past code? thanks
This is a bad install. I have run a spare pipe for future branch circuits but not for the homeruns when I have access.I was wondering if you could put like a 2'' pvc conduit on top and bottom of a new panel in a house for the homeruns? Is there a code to doing that? And would it past code? thanks
Why is it okay surfaced mounted, but not recessed. Why is it a minimum of 18" ? I know that code says so, but why does code say so?
I believe the 18" is to keep any arcing or fire from spreading that may start inside the panel.
Not sure why only for surface mounts. Historically this was done in this area either surface or recessed. For some reasons the inspectors use to allow it.
If you put a junction box on the end of the conduit there are no restrictions associated with 312.5(C). Derating would apply if the conduit exceeded 24".
You mean like a trough with nipples for a remodel?If you put a junction box on the end of the conduit there are no restrictions associated with 312.5(C). Derating would apply if the conduit exceeded 24".
... was wondering if you could put like a 2'' pvc conduit on top and bottom of a new panel...
312.5 Cabinets, Cutout Boxes, and Meter Socket Enclosures.
Conductors entering enclosures within the scope of this article shall be protected from abrasion and shall comply with 312.5(A) through (C).
(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) and not more than 3.0 m (10 ft) in length, provided all of the following conditions are met:
(a) Each cable is fastened within 300 mm (12 in.), measured along the sheath, of the outer end of the raceway.
(b) The raceway extends directly above the enclosure and does not penetrate a structural ceiling.
(c) A fitting is provided on each end of the raceway to protect the cable(s) from abrasion and the fittings remain accessible after installation.
(d) The raceway is sealed or plugged at the outer end using approved means so as to prevent access to the enclosure through the raceway.
(e) The cable sheath is continuous through the raceway and extends into the enclosure beyond the fitting not less than 6 mm (? in.).
(f) The raceway is fastened at its outer end and at other points in accordance with the applicable article.
(g) Where installed as conduit or tubing, the allowable cable fill does not exceed that permitted for complete conduit or tubing systems by Table 1 of Chapter 9 of this Code and all applicable notes thereto.