mbrooke
Batteries Included
- United States
- Technician
You would need a lot of technical substantiation to get any change in the EGC sizing table. It is very difficult to accomplish.
the current code for sizing EGCs does not go by wire size but by rating of the OCPD.
where are these rule numbers from anyway?
That table is for bonding conductor while you mentioned equipment grounding conductor. Maybe Canada calls the equipment grounding conductor a bond.
Yes, they did what the NEC should have done...changed equipment grounding conductor to equipment bonding conductor. The function of that conductor has nothing to do with a connection to earth.That table is for bonding conductor while you mentioned equipment grounding conductor. Maybe Canada calls the equipment grounding conductor a bond.
That is a technical change as you are basing the EGC size on the size of the ungrounded circuit conductor, but the current code is based on the size of the upstream OCPD.Technical substantiation just to get the code better organized?
For the record a table like that was approved in the first revision of the 2020, but deleted in the second revision as there are too many other changes in other parts of the code that have to be made for a table based on the size of the ungrounded conductor to work.
Point kind of is you really need to impress them to change something that has been the way it is practically forever. Only changes that have happened here were pretty minor changes here and there, you want to dump the thing out and put it back in a different manner.Technical substantiation just to get the code better organized?
Then you have plenty of time to work out all of those details...the PIs for the 2026 code will be due in September of 2026. Iti is highly unlikely that CMP 5 would accept a solution that requires multiple additional tables, and if they did, I would submit Public Comments in opposition. Additional tables would make the code more difficult to use and understand.Then have multiple tables for each condition. Motors, tap rules, welders, ect.
Man..Then have multiple tables for each condition. Motors, tap rules, welders, ect.
Man..
You really got to get out and get a job..
This stuff is making you crazy..![]()
And your the reason I'm going to click “ignore”...You're the reason the code is what it is today. Keep detracting![]()
Sure you have the right date there? Likely will be able to purchase a copy in September or October of 2025Then you have plenty of time to work out all of those details...the PIs for the 2026 code will be due in September of 2026. Iti is highly unlikely that CMP 5 would accept a solution that requires multiple additional tables, and if they did, I would submit Public Comments in opposition. Additional tables would make the code more difficult to use and understand.
Given the issues when a table like this was tried for the 2020 code, I would be very surprised if CMP 5 would ever accept a PI to use an EGC sizing table based on the size of the ungrounded conductors.
What is the confusion now? The rule is basically size with one table and per overcurrent device. EGC never needs to be larger than the largest ungrounded conductor for motors, taps, etc.Anyone willing to make a proposal for a table like this? Similar yet separate table for motors, tap rules and welder circuits. I think it would clear up a lot of confusion.