BatmanisWatching1987
Senior Member
- Location
- NJ
- Occupation
- Jr. EE
How do I calculate the Service Load Calculation, if I only know the square foot and not the Connected Load in kVA.
I have 3 Retail space, which one requires 600 AMP (120/240V/3P), and the other two retail spaces are 2,000 sq/ft and 3,000 sq/ft (120/240V/3P)
Would I use article 220.88 (New Restaurant) but I don't know the connected load since the space is empty and it's for future restaurant/retail.
This location has gas, so it won't be a all electric restaurant/retail
So for Lighting Load I can use Table 220.12 (2,000 sq/ft + 3,000 sq/ft= 6,000 sq/ft)
6,000 sq/ft * 2 = 12,000 VA
I would use 100% of the load based on Table 220.42
How do I determine the approximate Receptacle Load calculation, HVAC, etc
I have 3 Retail space, which one requires 600 AMP (120/240V/3P), and the other two retail spaces are 2,000 sq/ft and 3,000 sq/ft (120/240V/3P)
Would I use article 220.88 (New Restaurant) but I don't know the connected load since the space is empty and it's for future restaurant/retail.
This location has gas, so it won't be a all electric restaurant/retail
So for Lighting Load I can use Table 220.12 (2,000 sq/ft + 3,000 sq/ft= 6,000 sq/ft)
6,000 sq/ft * 2 = 12,000 VA
I would use 100% of the load based on Table 220.42
How do I determine the approximate Receptacle Load calculation, HVAC, etc