I need to run (design) a new feeder to run approx. 2000 ft underground to a new pumping station on an existing site. Load is approx. 80 KVA.
I had assumed a MV feeder would be most economical (there is 13.2 KV on site but all existing site loads are fed by 480 VAC). However, looking at conductor pricing online and in RSMeans it does not appear there is much savings as the minimum 15 KV cable size looks to be #2. Even with increasing conductor sizes for a 480 VAC feeder the savings to go with 13.2KV do not seem that large, once a transformer, switch, terminations at the remote location are factored in.
- Does 15 KV cable come in sizes smaller than #2?
- Am I missing some other savings associated with the higher voltage feeder?
I had assumed a MV feeder would be most economical (there is 13.2 KV on site but all existing site loads are fed by 480 VAC). However, looking at conductor pricing online and in RSMeans it does not appear there is much savings as the minimum 15 KV cable size looks to be #2. Even with increasing conductor sizes for a 480 VAC feeder the savings to go with 13.2KV do not seem that large, once a transformer, switch, terminations at the remote location are factored in.
- Does 15 KV cable come in sizes smaller than #2?
- Am I missing some other savings associated with the higher voltage feeder?