Those of you that know me well know that the fall of every three years is a very busy time for me, and that explains why you haven't seen me in quite some time. I would like to share with you a few of the Code changes that are upcoming in the 2011 NEC, from a book that I am editing currently. I hope you find this information useful:
New for the 2011 NEC?
The 2011 has some notable changes, many of which are quite significant. Some these more major changes are noted here.
What's new for the 2011 NEC?
During the 2011 NEC development process, several thousand changes and public comments were considered.
Fine Print Notes are now referred to as "Informational Notes." The term ?fine print? does not describe the function of a sentence or provision, it simply refers to the size of the text. By changing the term to ?informational note,? the Code makes it quite clear that these notes are intended to provide information and nothing else. The same logic applies to the change to ?informative annexes.? The style and layout of these notes and annexes have not changed, nor has the intent of them.
A new Article 694 for small wind electric systems has been added. This article covers small wind (turbine) electrical systems up to and including 100 kW. These systems can contain generators, alternators, inverters, and controllers.
A new Article 840 has also been added, which covers Premises-Powered Broadband Communications Systems. This article is similar to Article 830, but is often times more applicable. Expect for rare instances, Article 830 installations are made by a communications utility. Article 840 is intended to apply more regularly.
Only a few changes occurred in Article90. 90.2(B)(5) was revised to fix an error that occurred in 2008. This mistake was the removal of utility installations on Native American reservations, federal lands and similar areas from Code exemption. This change now gives the AHJ a means to exempt utility wiring in these areas.
Chapter 1--General
The definition of Arc-Fault Circuit Interrupter (AFCI) has been relocated from 210.12 to Article 100 because the term is used in more than one Article.
The definition of "bathroom" has been revised to add urinals, bidets, and similar equipment to the list of items that may be found in a bathroom. This change will result in a more uniform understanding of the Code.
"Bonding Jumper" is now referred to as "Bonding Conductor or Jumper." The 2008 (and previous editions) referred only to ?bonding jumpers,? which seems to imply a very short length of conductor used to bond things together. Although this may often be the case, they also may be much longer.
The term "grounding conductor" has been removed from the Code in not only Article 100, but also all other articles of the Code. The definition of "grounding conductor" seemed to apply only to communications systems and auxiliary grounding electrodes, yet this term was often used where "grounding electrode conductor" should have been used. Changes to the Code this cycle make for a more consistent and technically accurate document.
All "service Conductor" related definitions have been revised, deleted, or added. A real effort has been made to clarify that service conductors are those that are downstream of the "service point". Conductors upstream of the service point are not service conductors, they are utility conductors (and are not covered by the Code).
110.3(A)(1) Has been changed to reflect the fact some pieces of electrical equipment have special requirements, such as limitations on elevation, ambient temperature correction, power quality requirements or specific types of overcurrent devices. This information may be marked on equipment, or it may be in the product literature, or listing and labeling information.
Changes to 110.10 clarify that, in addition to the impedance of the circuit, the short-circuit current ratings of equipment are a vital part of determining whether or not a system or circuit can withstand the effects of a short circuit or ground fault. Specific examples of the types of things that warrant consideration are always better than referring to ?other characteristics.?
New provisions for finely stranded conductors have been added to 110.14, recognizing the fact that these conductors warrant special consideration.
A substantial change was made to Article 110 with the addition of 110.24. This new section requires that the available fault current must be marked at the service equipment of all installations, other than dwelling units. This change is intended to make sections 110.9 and 110.10 easier for the EHJ to validate.
The location of Table 110.28 (formerly 110.20) has been changed to Part II of the article, so that it applies only to equipment operating at 600 volts or less.
Chapter 2--Wiring and Protection
200.4 has been added to the Code, and it prohibits a single neutral conductor from serving multiple circuits (not including multiwire branch circuits). Nothing in previous editions of the Code prohibited a properly size neutral conductor from serving multiple circuits with ungrounded conductors of the same phase. This change eliminates this oddity from the Code.
As has been the case for the last several Code cycles, 210.8, covering GFCI protection, has been revised. The test and reset functions of the GFCI device must now be in a readily accessible location so that they can be tested monthly, as required by the product standard. A revision was made to the requirements of GFCI protected receptacles in patient care areas, and a new requirement for GFCI protection in nondwelling unit indoor wet locations has been added. Nondwelling locker rooms with associated showering facilities also require GFCI protection now, as do all 15A and 20A, 125V receptacles installed in service bays, garages and similar areas. The areas in which this applies is wherever electrical diagnostic equipment, electrical hand tools, or portable lighting equipment are to be used.
Clarifications to the AFCI requirements have been made, especially as it pertains to branch circuit extensions and modifications.
Changes to Part II of Article 225 will help Code users to understand the applicability of the requirements, and changes throughout Article 230 will help to delineate the difference between which conductors the Code covers and which conductors the Code doesn't cover.
A new term: "Bonding Jumper, Supply-Side" has been added to the definitions in 250.2. It is a new term, and can be found throughout Article 250.
Experienced Code users will recognize immediately that 250.30, covering separately derived systems, has been rewritten.
Experienced Code users may find themselves clicking their heels when they see that 250.56 is gone, but they may also see their smiles turn to frowns when they see that it was only relocated to 250.53(A)(2).
250.118 has been revised (again) to help to clarify the types of equipment grounding conductors (EGCs) recognized by the Code.