greekdaddy
New member
- Location
- Pennsylvania
I have a building that is fed from a transformer 300 feet away. Service conductors are 7 sets of four 600kcmil cable. 3 phases and neutral in each conduit.
The building is fed 480/277 from these conductors.
I am looking into a new ATS and GENERATOR that will be located 300 feet away near the transformer (this is done for space and aesthetic reasons).
Is there a way I can configure a non-separately derived system (3 pole, 4 wire ATS) to feed my building, not have figure out how to stuff an EGC in existing seven conduits and maintain the NEUT-GND bond in the building.
The bigger challenge is that the ATS has a 2500 AMP breakers that requires ground fault protection. Is there any way I can maintain this protection and keep bond in the building?
Also, does the requirement for ground fault protection allow me to monitor for faults at the building and shunt trip the feeder breaker?
Any help would be appreciated.
Parts of the code I have been tackling with are:
230.82(5) <-- allow ATS to be upstream and still consider my building to be "service disconnect"
250.142(A)(1) <- allow me to bond at building
250.122(F)(2) <- possibly try running 2/0 instead of 350kcmil
THANKS FOR ANY HELP YOU CAN PROVIDE!!!!
The building is fed 480/277 from these conductors.
I am looking into a new ATS and GENERATOR that will be located 300 feet away near the transformer (this is done for space and aesthetic reasons).
Is there a way I can configure a non-separately derived system (3 pole, 4 wire ATS) to feed my building, not have figure out how to stuff an EGC in existing seven conduits and maintain the NEUT-GND bond in the building.
The bigger challenge is that the ATS has a 2500 AMP breakers that requires ground fault protection. Is there any way I can maintain this protection and keep bond in the building?
Also, does the requirement for ground fault protection allow me to monitor for faults at the building and shunt trip the feeder breaker?
Any help would be appreciated.
Parts of the code I have been tackling with are:
230.82(5) <-- allow ATS to be upstream and still consider my building to be "service disconnect"
250.142(A)(1) <- allow me to bond at building
250.122(F)(2) <- possibly try running 2/0 instead of 350kcmil
THANKS FOR ANY HELP YOU CAN PROVIDE!!!!