I have a great project that I am about to start. It is a time and materials new resi. home - big money - approximately 6000 sq./ft. Unfortunately it starts asap and the cold weather is here. I am trying to configure the service and any insight to an easier way would be appreciated. Will be underground service - 400 amp (2 200 amp panels / 320 amp can) which will need to go to panels in mechanical room which is at opposite end of home from where service entrance will be. I am planning on one of two scenarios - #1= 320 amp meter main on service pedestal (fed via 2 sets 4/0 AL) at property line with 2 200 amp breakers and 2 sets of 4/0 AL run underground to 2 200 amp panels located in mechanical room. In this scenario I will hit ground rods at meter main and have a #4 CU ground wire run with each set of conductors to their panels. At panels I will hit each with #2 Cu to water main and also hit UFFER ground to one of them. My second scenario consists of me mounting a 320 amp meter can on outside stone face of house supplied by 2 sets of 4/0 AL. Then supply each 200 amp panel in mechanical room with a separate underground run of #4/0 Al grounding service at this point.
So what is the verdict? House is one level and over 160' long built into side of mountain.
So what is the verdict? House is one level and over 160' long built into side of mountain.