nsberkland
New member
- Location
- kansas city mo
I'm currently working on a house built in the 1930's. The electrical is a mess with a combination of a switch panel and a fuse box with most of it still being knob and tube. I'm running a new electrical line to the air handler in the basement. This is due to it currently being tapped off a light circuit which also feeds an outlet in the kitchen, a bedroom, and half the outlets upstairs. (There's no rhyme or reason to the current electrical setup :happysad.
My main question is I'm running 12NM through bored holes in the studs to the air handler. Once I get to the handler and run it down to where it enters the appliance and switch box will I run in to codes problems. Should this run in the basement be inside a conduit or is NM cable okay?
Any guidance would be appreciated.
My main question is I'm running 12NM through bored holes in the studs to the air handler. Once I get to the handler and run it down to where it enters the appliance and switch box will I run in to codes problems. Should this run in the basement be inside a conduit or is NM cable okay?
Any guidance would be appreciated.