I am designing the grounding system for a new industrial steel-framed building. The building is 100' x 25' with steel columns spaced 25' apart. Each column footing includes a rebar cage. There are also formed and poured walls between each column along the long walls.
Because the rebar is present in the footings I am planning to use it as my grounding electrode. My question is do I need to bond the rebar in the footing from each column? Can this bonding be accomplished by tieing together the footing rebar with the rebar in the walls?
I would typically design a ground ring around the perimeter of the building with pigtails to the rebar in the footings.
I need to run pigtails from the grounding system into 2 separate electrical equipment rooms as well.
Sorry for the lengthy explanation. Trying to satisfy a client who doesn't want a ground ring installed.