McCES

Member
Location
OHIO
I am designing the grounding system for a new industrial steel-framed building. The building is 100' x 25' with steel columns spaced 25' apart. Each column footing includes a rebar cage. There are also formed and poured walls between each column along the long walls.
Because the rebar is present in the footings I am planning to use it as my grounding electrode. My question is do I need to bond the rebar in the footing from each column? Can this bonding be accomplished by tieing together the footing rebar with the rebar in the walls?
I would typically design a ground ring around the perimeter of the building with pigtails to the rebar in the footings.
I need to run pigtails from the grounding system into 2 separate electrical equipment rooms as well.

Sorry for the lengthy explanation. Trying to satisfy a client who doesn't want a ground ring installed.
 
2008 NEC added a sentence in 250.52(3) which states that if you have multiple concrete encased electrodes that would serve as a grounding electrode, only one needs to be used. I suspect that they will all be tied together via building steel, but either way, as long as you use one, you are OK.
 
McCES said:
My question is do I need to bond the rebar in the footing from each column? Can this bonding be accomplished by tieing together the footing rebar with the rebar in the walls?
I would typically design a ground ring around the perimeter of the building with pigtails to the rebar in the footings.
I need to run pigtails from the grounding system into 2 separate electrical equipment rooms as well.
No, yes, not required, and each can be bonded to nearest accessible part of electrode.
 
Thanks for the insight guys. It just doesn't seem right that the tie-wired rebar woiuld be as effective as copper and cadwelds to bond everything together.
 