Dear Forum,
I have a rather lengthy question. Please bare with me. I am installing a
complex distribution system. Admittedly, it is beyond my normal scope of
daily duties. It is my hope to make this clear as can be when describing the
task at hand.
From and at a pad mount xfmr's secondary of 480v I will be installing a 200
amp fused safety switch. The conductors will travel underground 225' to a
new wood frame single story bldg. Inside the building I will install an
additional 200A fused safety switch then to a 150kva xfmr that will be in
close proximity and have a secondary of 120/208. From this new SDS
transformer I will be installing a 400 amp MB panel then to a ML sub panel
rated at 200A. All components will be in close proximity <10'. This is all
specked out in the drawings. There is a note stating that "Connections shall
be neutral/ground bonded". I understand the terms "System bonding jumper",
"Equipment ground conductor" & Parallel path potential.
My question: Where should I Neutral/ground bond and where should I not?
This is a commercial building and will be 3 ph. throughout. The new
transformer must be neutral/ground bonded as per manufacturers
recommendation.
Thanks
Rich
I have a rather lengthy question. Please bare with me. I am installing a
complex distribution system. Admittedly, it is beyond my normal scope of
daily duties. It is my hope to make this clear as can be when describing the
task at hand.
From and at a pad mount xfmr's secondary of 480v I will be installing a 200
amp fused safety switch. The conductors will travel underground 225' to a
new wood frame single story bldg. Inside the building I will install an
additional 200A fused safety switch then to a 150kva xfmr that will be in
close proximity and have a secondary of 120/208. From this new SDS
transformer I will be installing a 400 amp MB panel then to a ML sub panel
rated at 200A. All components will be in close proximity <10'. This is all
specked out in the drawings. There is a note stating that "Connections shall
be neutral/ground bonded". I understand the terms "System bonding jumper",
"Equipment ground conductor" & Parallel path potential.
My question: Where should I Neutral/ground bond and where should I not?
This is a commercial building and will be 3 ph. throughout. The new
transformer must be neutral/ground bonded as per manufacturers
recommendation.
Thanks
Rich