O omancillas77 New member Location inland empire Mar 5, 2015 #1 Can a 200 amp single phase load center be fed from a 100 amp main service??
Smart $ Esteemed Member Location Ohio Mar 5, 2015 #2 Yes, if by "100 amp main service" you mean the OCPD associated with the service disconnecting means is rated 100A.
Yes, if by "100 amp main service" you mean the OCPD associated with the service disconnecting means is rated 100A.